Title: 1HP motor on a 120 volt 15 amp outlet ?
Post by: veggie on March 28, 2023, 07:12:37 PM
Anyone running a 1HP motor on a standard 15 amp wall outlet?

In my case its a basic 120 volt, 1800 rpm cap start motor.
I have not bought it yet, and I'm wondering if my wall outlet can start it.
Running amps is fine ( 9.7A) but I'm not sure if the capacitor start will suffice to get it going.

Whats the most HP you have started (under no load) with a wall outlet.?
Title: Re: 1HP motor on a 120 volt 15 amp outlet ?
Post by: Henry W on March 28, 2023, 09:18:45 PM
Ran Rockwell Delta horizontal/vertical belt sanders with 1 hp capacitor start motors. And Delta contractor's table saws with 1 hp capacitor start electric motors on 15 amp wall outlets. Shortest wire length and 12 gauge wire helps.

I have run 1 hp capacitor start motors on wall outlets with 14 gauge wire with no problems.

Title: Re: 1HP motor on a 120 volt 15 amp outlet ?
Post by: veggie on March 29, 2023, 07:51:50 AM

Thanks Henry  :)
Title: Re: 1HP motor on a 120 volt 15 amp outlet ?
Post by: Tom Reed on March 29, 2023, 03:06:01 PM
Got a 1 hp motor on the drill press. When belted for top speed it has some trouble starting, other than that no issues. It's running of an Outback inverter since we're off-grid.
Title: Re: 1HP motor on a 120 volt 15 amp outlet ?
Post by: mobile_bob on March 30, 2023, 07:02:56 PM
it also depends on what the motor is connected to.

a 1hp motor connected to a compressor that is asked to start at perhaps 120psi and cut out at 150psi may have a difficult time starting up, that is if it doesn't have some sort of unloader system.

blower motors also have a harder time starting,

high efficiency motors also have higher starting amps requirements.

what do you have in mind for the load for this new motor?

bg
Title: Re: 1HP motor on a 120 volt 15 amp outlet ?
Post by: veggie on March 31, 2023, 07:41:51 AM
Hi Bob,

It would be driving a rotary gear pump for oil transfer. only 10 psi.
The actual demand is about .6HP, but I was concerned that a 1HP on a 15 amp breaker might trip even when unloaded due to inrush current demand. Full load amps (FLA) is 9.7
Some say in rush current is up to 300% of FLA. Others say size the breaker for FLA +25% which in this case would be 12.1 amps.
Title: Re: 1HP motor on a 120 volt 15 amp outlet ?
Post by: Henry W on March 31, 2023, 08:07:15 AM
I would think you would be able the use a 3/4 hp motor.